81. The ring main system is used in power distribution because it--
ব্যাখ্যা: There are less voltage fluctuations at consumer terminals. The system is very reliable as each distributor is fed via two feeders. In the event of fault on any section of the feeder, the continuity of supply is maintained
is reliable for continuity of supply
gives better voltages regulation
results in less feeder losses
all of the above
88. Which of the following is not the distribution system, normally used-
ব্যাখ্যা 2 AC distribution system can be classified as- -Single phase-2 wire system -Sinele phase-3 wire system -Two phase-3 wire system -Two phase-4 wire system -Three phase-3 wire system -Three phase-4 wire system
3 phase 4 wire
Single phase-3 wire
Single phase -4 wire
3 phase-3 wire
89. The distribution transformer is generally connected in--
ব্যাখ্যা: The distribution transformer is generally connected in deta/star. In secondary side, star connection is required which has neutral point. From this star connection. Voltage is used by consumers.
Delta/Delta
Star/Delta
Star/Star
Delta/Star
90. TStability of a system is not affected by-
ব্যাখ্যা: Stability of power system is affected by- -Reactance of transmission line -Reactance of generator -Excitation of generator -Input output torque.
Reactance of line
Losses
Reactance of generator
Output torque
91. The most severe unsymmetrical fault is-
ব্যাখ্যা: Symmetrical three phase fault is the most severe kind at the transmission lines, while for faults occurring very close to the generating station or synchronous generator, single line to ground fault is the most severe.
single line-to-ground fault
line-to-line fault
double line-to-ground fault
none of the above
96. The common fault is overhead distribution system is-
ব্যাখ্যা: About 50-55% fault in overhead distribution system is one phase to earth fault and 12-15% fault is phase in phase fault
phase to phase fault
one phase to earth fault
all phase short circuited
none of the above
97. Capacitance of a transmission line is the result of-
ব্যাখ্যা: Capacitance of a transmission line is the results due to the potential difference between the conductors. The conductors get charged in the same way as the parallel plates of a capacitor, capacitance between two parallel conductors depends on the size and the spacing between the conductors
Potential diference between the conductors
Current flow in both conductors
Current flow in either conductors
Charge per unit current
99. Routing means connecting-
ব্যাখ্যা: Routing is the process of selecting a path for traffic in network, circuits or different equipments.
Circuit or equipment to earth
Impent to earth
Circuit to earth
None of the above