84. The ring main system is used in power distribution because it--
ব্যাখ্যা: There are less voltage fluctuations at consumer terminals. The system is very reliable as each distributor is fed via two feeders. In the event of fault on any section of the feeder, the continuity of supply is maintained
ব্যাখ্যা: Stability of power system is affected by-
-Reactance of transmission line
-Reactance of generator
-Excitation of generator
-Input output torque.
90. Which of the following is not the distribution system, normally used-
ব্যাখ্যা 2 AC distribution system can be classified as- -Single phase-2 wire system -Sinele phase-3 wire system -Two phase-3 wire system -Two phase-4 wire system -Three phase-3 wire system -Three phase-4 wire system
94. Capacitance of a transmission line is the result of-
ব্যাখ্যা: Capacitance of a transmission line is the results due to the potential difference between the conductors. The conductors get charged in the same way as the parallel plates of a capacitor, capacitance between two parallel conductors depends on the size and the spacing between the conductors
ব্যাখ্যা: Symmetrical three phase fault is the most severe kind at the transmission lines, while for faults occurring very close to the generating station or synchronous generator, single line to ground fault is the most severe.
96. The line voltage on the LT side of a distribution transformer is--
ব্যাখ্যাঃA LT (Low Tension) line is a low voltage line and ITT (High Tension) line is a high voltage line. In LT supply is of 400 volt for three-phase connection and 230 volt for single-phase connection. High tensione HT supply is applicable for bulk purchase who need 11 kilo-volt (kV).
100. The distribution transformer is generally connected in--
ব্যাখ্যা: The distribution transformer is generally connected in deta/star. In secondary side, star connection is required which has neutral point. From this star connection. Voltage is used by consumers.